This means that the receiver does not supply the voltage for the door strike or magnetic
lock. You will need a power supply that supplies the correct voltage and sufficient
current to operate the door strike or magnetic lock. You can use a single power supply
for both the receiver and the door strike or magnetic lock if both the receiver and the
lock use the same voltage and the power supply provides sufficient current to operate
both devices.
You will switch one leg of the power supply for the door strike or magnetic lock through
the relay on the receiver. The wiring would be connected as follows:
1. Wire one side of the power supply to the common on the receiver relay.
2. Wire one side of the strobe light or siren to the N/O (normally open) contact on the
receiver relay.
3. Wire the other side of the strobe light or siren to the other side of the power supply.
NOTE: Make sure that the current draw of the door strike or magnetic lock does not exceed
the current rating of the relay in the receiver.